Miprom 21.... again
|
Joined: Nov 2016
Posts: 105
Goat
member
|
member
Joined: Nov 2016
Posts: 105
|
Once again have this Miprom giving me heck.
13 stop, 10,000lb capacity, 2:1 basement machine, HPV900
Have Kone Service Tool intergrated into a computer purchased from Kone Spares.
Background of elevator *had issue with MSU board giving only positive DC command to drive(was fixed and ran fine) *the issue listed below started happening(changed CPU, MSU, Relay Pilot Board, did not change) *found bad traveling cable(replaced both, as they each had their own separate issues. ) Did not fix issue. *Replaced cartop encoder during the traveling cable change out.
Symptoms *from 9th landing down, while on inspection, will run for approximately 2 seconds then shut down, waits 5 seconds for reset then will run another 2 seconds. Up and down direction.
*around the 9th landing, car will start running a touch longer, then right about 10, will run nonstop as it should in up or down direction
*10th landing is a little over halfway of the entire rise.
*No faults are listed under motion excuses.
*No faults show on the drive(No overvolt, torque limit reached, etc)
*If I pull the cartop encoder off the rail, elevator will run at bottom of the hoistway without stopping every 2 seconds.
Service took does not allow me to adjust drive, as it is a magnatech and not a Baldour. Any help would be greatly appreciated.
|
|
|
#26163 - 03/10/19 08:01 PM
Re: Miprom 21.... again
[Re: Goat]
|
Joined: Jan 2014
Posts: 736
Rolly
old hand
|
old hand
Joined: Jan 2014
Posts: 736
|
|
|
|
#26184 - 03/12/19 08:23 PM
Re: Miprom 21.... again
[Re: Goat]
|
Joined: Nov 2016
Posts: 105
Goat
member
|
member
Joined: Nov 2016
Posts: 105
|
Quick update, I was able to work a little more on it. As of Sunday, I was able to find a list of parameters for the drive, that was originally setup. Everything is in order on that side.
I was unable to find anything regarding what level my tool is. I looked up the World Tool. Going to be hard to convince my customer to fork over 6k for another tool. This is my only Miprom 21. So I dont forsee my company purchasing the tool if the customer will not pay.
I am able to watch the motion excuses window while running on inspection. I am running it from the controller. I never see a motion excuse come up other the the contractor reset timer. It drops out like it loses its safety string, but everything on that has been checked good with a meter.
I need to check the bearing on the cartop encoder wheel. When I changed the encoder, I payed some attention to everything checking my tension and such, and didn't see any abnormal play. I will check that again though. It just seems it's not an encoder issue, as it acts fine in the top half of the hoistway. I am open minded and not putting on blinders. It very well could be an encoder issue. I just figured the miprom would come up with some sort of fault.
My next trip out there, its 3 1/2 hours away, I will check encoder bearing, jog adjust parameter, and the timing of the P and SB relays.
Thank you all for the info yall are providing.
|
|
|
#26198 - 03/13/19 05:06 PM
Re: Miprom 21.... again
[Re: john jay]
|
Joined: Nov 2016
Posts: 105
Goat
member
|
member
Joined: Nov 2016
Posts: 105
|
Have you checked the load weighing ? Does this only happen on inspect? Load weigher is not hooked up. Has been that way since we took over the job 3 years ago. So no telling how long it has not been connected. I will check the sensitivity of the optical readers. And yes a new floor table was ran. I will check the DBG. It is unlikely that the rails have moved dus to the jumbo rails having a bracket every 6 feet but anything is possible. I was able to convince my customer to purchase the World Tool. Looking at the manual for it, it definitely seems better than the junky KONESpares tool. The tool actually has you select what region you are working in, KONESpares just connects without any selections. I will be headed back out there once the world tool comes in. Once again thank yall for the guidance.
Last edited by Goat; 03/13/19 05:07 PM.
|
|
|
#26208 - 03/14/19 01:16 AM
Re: Miprom 21.... again
[Re: Goat]
|
Joined: May 2013
Posts: 224
Jcjmowrey
enthusiast
|
enthusiast
Joined: May 2013
Posts: 224
Atlanta ga
|
Once you get the tool, download the miprom 21 quick reference app of your phone’s App Store. The freedom tool comes with a manual but this app makes it easier.
If all else fails, read the instructions
|
|
|
#26328 - 03/28/19 05:00 PM
Re: Miprom 21.... again
[Re: elmcannic]
|
Joined: Nov 2016
Posts: 105
Goat
member
|
member
Joined: Nov 2016
Posts: 105
|
Bummer,
Seems this is vane reader issue is new right? Previously you did run a floor table, and there was no mention of it not being saved, so what’s changed other than tool type? Both optic readers are set at “max”...is the car speed for inspection set to about 25fpm for the learn? So when you inspect the car to the bottom and onto the DDL to start the floor table build, it won’t see any vane going up correct?
Yes previously was able to run a floor table, but somehow the table was lost. Im assuming with the swapping and changing of everything it was lost? That is correct that starting on my down directional limit, and all the way up to my up directional, no vanes what so ever are read using the vane reader check. I have had ongoing issues with this elevator ever since taking it over 3 years ago.
|
|
|
#26334 - 03/28/19 10:10 PM
Re: Miprom 21.... again
[Re: john jay]
|
Joined: Nov 2016
Posts: 105
Goat
member
|
member
Joined: Nov 2016
Posts: 105
|
If you swapped the CPU the floor table and all the field programmable parameters are gone. The floor table is on a removable chip I think it is at U37. or U18, depending on the age of the install. You can also read read the vanes while making a new floor table. Every floor must say good as it goes past the vane. If one says bad that is the vane you need to look at. That's the thing, every single vane, all 12, show bad. Like it is not processing in the CPU. That's while doing the vane reader check. I attempted to use the old dallas ram chip but one of the prongs broke off taking it out of the old board.
Last edited by Goat; 03/28/19 10:11 PM.
|
|
|
#26336 - 03/29/19 12:47 AM
Re: Miprom 21.... again
[Re: john jay]
|
Joined: Nov 2016
Posts: 105
Goat
member
|
member
Joined: Nov 2016
Posts: 105
|
You have lost all the original field programmable parameters. So you need to go through and re-install them. Things like the motor name plate RPM, Pulses per revolution, motor encoder drive wheel resolution if it is friction driven, and on and on. you need to get a hold of the parameters that were originally installed by the adjuster. Then it is easy to copy them to the CPU and Drive they both have to read the same. Good Luck. Well I guess the only good thing is that drive parameters are correct. I will start rummaging through everywhere on the jobsite and hope to obtain anything regarding the parameters. Thanks for yalls help.
|
|
|
|
|