Any wise one out there that can help a kid out? I have a Miprom 1. During a demo the fire service and sensors alarms were cut and car parked on second floor as programmed to. They could not get fireservice back on so building to disconnect fire alarm and smoke sensors completely. In fact, it locked 10 cars in fire service. But the other were Otis and Elevator Control. And there was prints for those. I saved the best for last, the Miprom 1. It is a 4 stop hydro front operating doors only. Doors O/C on test mode only. No car top inspection. I have no input or out puts lightning up. On "Power Supply Connect Board "I have 115AC onL2B, L2A, & SS. 21DC on V+ and -3DC on V-. Which seems good, but no specific prints to go by. So I'm just living up to my name. On that same board, 2 toggle switch. Sw1 Sw2 , when flipped up lights up but fades out after 1or2 seconds. Non of the red/green LEDs light up but I do get voltage to some terminals.
Thanks I'll give that a try. But honestly I'm just assuming it's in fire service because all other 7 elevators were indicated on LCD screen or service tools. Wouldn't LED (red) on input board show ? But like I said they had specific prints which was a lot easier to troubleshoot the others.
if the inputs are not lighting up it is possible you have a bad power board, or a bad card rack. Sometimes a bad input can cause this also. Did you try pulling all the inputs and re-inserting them one at a time?