0 registered members (), 13 guests, and 0 spiders.
Topics6,494
Posts36,781
#29445 - 06/11/20 12:58 AM Dover Compumatic
EMEEL LLC Offline
EMEEL LLC  Offline
Hi, with Dover computamatic controllers, I have problem with 4 elevators/15 story building. the dispatcher unit looks like disabled.
All elevators are running in wild operation (The elevators are running continuously between the floors and never stops , and the hall calls still stuck on and never cancel the calls.
We checked all the wiring between the dispatcher unit and the controllers; and even if we turn the dispatcher off the wild operations is still.
I could NOT figure out what is the problem and how we can re communicate these elevators with the dispatcher.
Thanks for helping,,,
#29447 - 06/11/20 11:36 PM Re: Dover Compumatic [Re: EMEEL LLC]
What city are you in?
#29448 - 06/11/20 11:37 PM Re: Dover Compumatic [Re: EMEEL LLC]
Check relay ATO, is it in? are all your wire contacts in ATO in good shape?
#29449 - 06/11/20 11:48 PM Re: Dover Compumatic [Re: EMEEL LLC]
voltage from ATC to S+ ???
#29450 - 06/11/20 11:49 PM Re: Dover Compumatic [Re: EMEEL LLC]
condition of NP Relay
#29526 - 06/27/20 07:31 PM Re: Dover Compumatic [Re: EMEEL LLC]
EMEEL LLC Offline
EMEEL LLC  Offline
thank you very much.
i got the problem solved.
some wire in dispatcher came off by loose connector.
Thank you very much
Page Time: 0.030s Queries: 16 (0.010s) Memory: 2.6837 MB (Peak: 2.8513 MB) Zlib disabled. Server Time: 2024-04-18 23:45:39 UTC