Hello, today I had the time to go to this lift again to make some more tests
If I
Make OCSS not aviable it could be a drive fault, brake fault or 8LS fault I get error code 0100 OpMode NAV. I did notice that this arrer is also active after INS before the correction run starts.
If I
Prevent the car from running in EPO (emergency power) I get error code 0101 EPO shutd. I noticed that in group or dublex the next car is allowed to recover after this error.
If I
Make UIS and DIS signal active without DZ I get error 0216 DZ missed. I noticed that this happens when LV relay is not working correct.
If I
Prevent brake current or valve current during the run I get error code 0255 brake-fault.
If I
Put current to brake or valve during the stop I get error code 0227 NST:NoBrake
If I
Make 1LS and 2LS inputs active at the same time I get error code 0228 1LS+2LS on.
If I
Make LSVF-W Drive not ready I get error 0231 LSVF-W:/DR, or during the decceleration the car speed was too high to perform ADO or relevelling I get error 0232 LSVF-W:/SC. And when I power LSVF up I get 0233 LSVF_W:P-ON.