Make a fault to drive unit(motor control) I will loose the OP signal and I get error code 0234 OP lost.
If I
Mix up the interface betwen the LCBII and drive unit I get error code 0235 OP/T fault
If I
Open the landing door lock in fast run I get error code 0237 /DW in FR but if cut the DW signal during the slow run I get error code 0238 /DW in SR
If I
Make signal DFC low and SE high while the door is opening or fully opened I get error code 0300 DBP:dfc_SE. This is when the door bypass was found inactive.
If I
Make door close limit (DCL) active when the door is fully open I get error code 0301 DCL in []
If I
Make the DW signal active when the doors are open I get error 0302 DCS:DW err
If I
Make the DOL (door open limit) active when the doors are closed I get error code 0304 DOL:alw on. This also happen when I remove DO2000 fuses.
If I
Open the landing door or bridge the car door contact I get error code 0306 Hwy-Access.
...thats all for today. Next time I will test the blinking events of this system.