As a technician with an independant l ft company in the UK I have inherited several schindler Bionic 5 MRLs. I had to attend one today which had been recently working.
The controller indicates that the lift is on test, but all the switches have been returned to normal. I consulted the manual and followed the instructions to reset the test. This had no effect.
The error light is pulsing regularly and the ISK section of the safety circuit is open. I traced this to the REC .
Can anyone help me with this problem.
Also, I have a PDA with the software to interrogate Thyssen controllers, and I would appreciate it of anyone has a copy of the Schindler test tool software that I could install on this.
Unfortunately, as we all know, schindler won't be helping anyone who has gained service contracts on their equipment so any help from you chaps would be greatly appreciated.