Easy, that is not a TKE procedure by any means. I am a new install adjuster and I can guarantee every single TAC32 has a thumb drive with everything on it, including the manual. Our state requires it to be left onsite as part of the MCP.

What faults are generated? Sounds like the SP took a royal deuce. You can try to redo it by moving the top left jumper by SP to the 1-2 pin, then type SPC into remote fast window of IMS. Replace the jumper to 2-3. It should say sp config. In the remote fast, cycle the power. If you do not have IMS send me a private message, I can step you through using the UIT. If this doesn't clear it up, you lost the CPUA or the man card it sits on...drawing a blank, think it's IOD for the TAC 32, or its IOC, one is for 50-04, other is for the 32.