1 Run the elevator to the bottom floor. Give call from LCECPU user interface.
2 Turn the elevator to RDF drive from switch 270.
3 Use the RDF drive for positioning
elevator so that:
• Switch 61U is ON.
• Switch 30 or B30 is ON (or both)
• Synchronisation switch 77N is ON
• Synchronisation switch 77S is ON
Same position as with set-up.
4 Give start command from LCECPU User Interface menu.
• 5_5_0 -> 1
5 Turn the elevator to the normal drive from switch 270.
Deceleration distance learning mode starts.
• The elevator starts to run up and down using full speed and service speeds
performing several steps to the top floor. After few seconds the elevator
drives back to the bottom floor.
NOTE! Prerequisite for deceleration distance learning is that successful set-up has been
completed.
• Turning elevator to inspection drive immediately terminates learning mode.
• Any fault immediately terminates learning mode.
• During learning mode sequence elevator most likely stops outside door zone.
• The elevator does not even try to stop at door zone.
• LCECPU position indication shows current elevator position.
• LCECPU User Interface buttons are disabled.
• If learning mode terminated before successful completion it has to be restarted from step
1.
NOTE! IF V3F10 FULL or SERVICE SPEED IS PERMANENTLY CHANGED AFTER
DECELERATION DISTANCE LEARNING THEN DECELERATION DISTANCE
LEARNING HAS TO BE PERFORMED AGAIN.
Temporary change of service speed does not necessitate new learning drive provided that
service speed is set back to original value (=value that was effective during the learning
mode).