136 SPU thermal switch fault. The SPU temperature is too high.
137 There was a one floor run detection but no slowdown when the position changed.
Used on KM White overlay controllers only!
138 Selector error for Westinghouse overlay controller.
139 Terminal position error for Westinghouse overly controller.
140 ETS Up limit error: The switch did not activate when expected from the position count
reference. Check switch activation from cam and EUR parameter.
141 ETS Up Software limit error: The switch activated but it did not match the position count
reference. Check switch activation from cam and EUR parameter.
142 ETS Down limit error: The switch did not activate when expected from the position count
reference. Check switch activation from cam and EDR parameter.
143 ETS Down Software limit error: The switch activated but it did not match the position count
reference. Check switch activation from cam and EDR parameter.
144 Not used on Futura
145 LTR parameter rate set too low during emergency deceleration at terminal limit.
146 DZ relay failed on (for 2000 Code Compliant)
147 CEC String did not drop when expected (for 2000 Code Compliant).
148 CGDL (Gate Door Lock Contact) did not drop during CEC test (for 2000 Code Compliant).
149 110 Percent governor over-speed switch tripped (for 2000 Code Compliant).
150 Not Used on Futura™
151 Not Used on Futura™


Here you go. The extended version. I've had this problem before. change out your DZ sensors. Intermittant faulty one.

Best of Luck!
NYguy