Replaced this VF33BR drive on a 400A. Entered all drive system parameters, did an end commission, said complete, still have red & green light on on drive and either a 700 or 726 error on SMLCD. When I check drive parameters, the inverter type is set to none. If I change it, it says OK but when I go back in it’s set to none again. Can’t get it to take parameters from CPU either after double reboot or draining super cap. From doing some research, maybe the temp setting has defaulted to 0 so won’t let me change inverter type? Looks like I may be able to change the temp setting without the CADI if the software is newer than 2.10. My next idea is maybe the drive software isn’t compatible with controller software. Can’t tell you what either of them are until I go back on Monday but I have a chart to see if it is compatible and I think I can load drive software if it isn’t. Maybe then the parameters would transfer to the drive automatically after a double reboot?

Any insight or suggestions would be greatly appreciated.