I'm having an odd issue with the Phase 1 fire service on an LRV4. It's a 2-stop, front-opening only, phase 1 switch on the 1st floor. When I turn it on with the switch, the car nudges the door closed, and drives itself into the pit. It runs normally otherwise - PI reads correctly as well.

I've checked the dip switches on the board in the car station, and I have a nearly identical car at another job with which I've compared the settings and wiring.

The only thing I can think of is one of the hoistways switches (L9S if I remember correctly?) maybe tells the CPU where the car is at in the hoistway, so the car doesn't really know it's on the 1st floor? All the system has is the 2 mechanical switches at the top and bottom of the hoistway, LD, LU, DZ, and the L9S. They all appear to be working properly, including L9S. But maybe I'm barking up the wrong (switch) tree.

Any ideas?