Network supervision or roll call operation has detected that the Fire Status Panel (LCE
FSP) is not responding. Possible causes:
• Defective LCE FSP board
• Defective LON network wiring
• Defective Repeater. Also make sure repeater and 24-volt switching power
supply are not located adjacent to one another. If so, move the repeater to the
opposite end of the DIN rail.
• Try pressing the small white reset button on the lower LH corner of the FSP
board. If that corrects it but problem returns later, replace FSP board.
• Missing 24 volt power
• LON download corrupted