That looks correct to me.
In door operators usually the
DCL switch is Normally Close and
DOL switch is Normally Open.
This means when the door is fully closed and DCL is active, obviously DOL is not active and would be open (because it is NO contact), so it’s NC would be close and you see 24v on NC DOL.
When the door is fully open and DOL is active, obviously DCL is not active and because it is an NC contact it outputs 24V.

If it doesn’t match with your controller, I think you should reach out to Smartrise support. Good luck with that