#6469 04/04/13 06:41 PM
Service Manager
Service Manager
Have a 3 stop LRV3 at least once a month gets stuck with doors closed,exit elevator light on, if doors are forced open nudging buzzer goes off and door nudges close and thats it!!! have to reset controller in order to run. i know its not much info but thats all i have. any idea what may be the cause? maybe bad magnetic sensors on COP? any help or suggestions would be greatly appreciated.
bk2fla #6484 04/05/13 01:48 AM
You unlucky bastard.
Do you know if it was upgraded to the lrv 4?That would be the pc controller behind the cop.
Check your door locks,gate switch and cam switches in the door operator,assuming it's the otis version of gal,QL.
Reseat the plugs on the pc board behind the cop.
just something I have found on LRV'S, 75% of the problems are caused by the door open, door close relays. these are the 2 black plastic modules that plug in to the relay board. I always replaced these before doing anything elese.
I second that on the connections ..not only the lock whipe but the wire terminals ...tighten all controler wires ..
tony #6525 04/08/13 12:37 PM
Service Manager
Service Manager
@elevatedone yes it has the pc board behind the cop.
i will check all that was suggested. thanks for the help guys.
@john jay @tony
bk2fla #6604 04/15/13 06:16 PM
Had a similar problem. Check your voltages off the power supply above your processor board. If the voltages are fine, possibly the processor board.
Len Offline
..upgrade to an LRV4..processor..have had this problem before..this fixed a lot of issues..might be hard to find a replacement LRV3 processor board....
PHP: 8.3.33 Page Time: 0.023s Queries: 28 (0.008s) Memory: 3.0267 MB (Peak: 3.5923 MB) Data Comp: Off Server Time: 2026-09-21 05:21:57 UTC
