0 members (), 44 guests, and 3 robots.
Previous Thread
Next Thread
#7672 07/13/13 03:30 AM
V Offline
hey all,i am having a problem with an Otis gen2 controller,we got a call that its not working when I check it the led in the controller saying its in inspection,but all the switches is in the normal position
vatorcorp #7673 07/13/13 04:58 AM
Call your service tech to troubleshoot the issue
sbrmilitia #7674 07/13/13 05:52 AM
V Offline
i have check the inspection button on the car and in the comtroller and it was ok
vatorcorp #7675 07/13/13 10:28 PM
Sounds like something else is activating inspection, like you CPU. Are you a elevator Mechanic? If not please call someone who is! Your safety as well as others is more important then saving a couple hundred dollars!
jkh #7677 07/14/13 12:03 AM
V Offline
yes it was a blown fuse on the cpu<yhanks much jkh
PHP: 8.3.36 Page Time: 0.083s Queries: 24 (0.016s) Memory: 3.0136 MB (Peak: 3.5904 MB) Data Comp: Off Server Time: 2026-11-06 19:01:15 UTC