#11359 07/18/14 01:44 AM
Have a car getting selector error 72 at times. Getting other errors on CLC. Unit will run up about 2' and just slow down then speed back up make a bad landing at the 2nd floor. It is a 2 stop with dual jacks thought it was the sensor, but that didn't pan out? I have replaced the selector board, main and aux. sensor board. Problem still exists, also checked the switch tree.....Thinking of replacing the CLC ? Oh does the same thing in the down direction? Any Ideas? And every 20 or so runs it will make a few normal landings?
halfpick #11362 07/18/14 03:01 PM
Check the directionals limit. Sounds like it could be seeing both in the same state.
pdq1600 #11368 07/18/14 04:28 PM
yes maybe stuck in the directional limit switch tree
djenergy #11399 07/19/14 10:02 AM
Did you check the back card and the orientation of the two magnets?
cucuvator #11402 07/19/14 03:20 PM
Well, after talking to several mechanics on the phone. And conversing back and forth! I was losing the FST relay contacts on the relay board. It sure gave me a bunch of crazy errors!
halfpick #11404 07/19/14 03:25 PM
Good find, thanks for the update...