#13646 03/13/15 02:17 AM
Anybody had a MCE lose the rudedncey safe check in flight and not reset just tries to resest the system but never sometimes it will get a emergency brake flt but no emergency brake
Derick #13647 03/13/15 03:13 AM
Flaky governor switch. Put a trap relay across the overspeed switch. Could be an encoder or brake issue also, the controller might think it is overspeeding.
NewMech #13649 03/13/15 11:51 AM
yes thought of that we ruled out a safety circuit on the car and machine room thinking it may be a ribbon cable or bad board we also changed relays in controller
Derick #13740 03/27/15 03:38 AM
Troubleshooter
Troubleshooter
check supply power for dips. Also check you traveler for cuts. As it passes whatever has damaged it, you can hit a fast ground (and not blow the fuse due to length of time and wire) and drop voltage to a level that causes you misery.
J Sand #13893 04/10/15 07:37 PM
I had a similar issue. Started happening every once in awhile then about everyday. I replaced the power supply in the controller and it never happened again.
local yocal #13954 04/16/15 12:31 AM
i had some odd stuff going on and a MCE tech. told me to flip the ribbon cables!!! oddly enough i never had another callback on that unit.
PHP: 8.3.36 Page Time: 0.030s Queries: 26 (0.008s) Memory: 3.0196 MB (Peak: 3.5927 MB) Data Comp: Off Server Time: 2026-11-05 04:28:54 UTC
