#14038 04/30/15 12:59 PM
Liscensed Journeyman
Not having any real issues at the moment, except 1057 and 1062, of which both are encoder issues, top and bottom. Never shutdown though. 150 fpm. Don't have a IMS setup for the tach 20, but have the floppy loaded on a thumb. So i have to do every thing off the not so user friendly user interface. Looking for the schrack part#, who would the vendor be. Any help? Thanks
JustWolf #14039 04/30/15 03:29 PM
Found the part#s
JustWolf #14040 04/30/15 04:43 PM
Encoder on a tac20 hydro controller??? Only encoder I am aware of is the door encoder. Think you are using the wrong fault log chart.
Silly #14041 04/30/15 05:47 PM
Silly,
Good to know it's a Tac22 chart and I was lead to believe it was the same as 20. Got to do some digging. Thanks
JustWolf #14043 04/30/15 11:57 PM
The selector has an encoder count also. the 1062 is usually a gap in the slowdown magnets, or sometimes to short of a slowdown distance. The Tac22 is a mod version of Tac20A(non-lon). You need a tool to look at fltn command to get better info on the faults.
PHP: 8.3.33 Page Time: 0.026s Queries: 24 (0.006s) Memory: 3.0148 MB (Peak: 3.5925 MB) Data Comp: Off Server Time: 2026-09-21 00:51:27 UTC
