October
4 5 6 7 8 9 10
11 12 13 14 15 16 17
18 19 20 21 22 23 24
25 26 27 28 29 30 31
10,053 Registered Users
Topics7,404
Posts41,025
Members10,053
#15362 11/10/15 12:57 PM
Tac 20, Siemens soft start has LCD screen blank.
Have safety string, car floor level in basement, no voltage at terminal 1 and 3 on Siemens terminal strip. Fault contactor bad?
No fast tool at moment.
Any suggestions?
chicago #15363 11/10/15 01:10 PM
Liscensed Journeyman
Siemans Class 72 logic board,see the post 7/30/2015 in technical questions. See if it looks like that.
JustWolf #15364 11/10/15 02:09 PM
Yes, it looks like that. But if I don't have 110 vac at terminal 1 & 3 on starter problem before it gets to starter?
chicago #15366 11/10/15 03:37 PM
Check for 120Vac on terminals 1 and 3 on the starter after powering up or a reset. A tac20 will power it up after about 20 or so seconds. Then some faults will cause to tac20 to remove the power due to the certain fault. Also check to see if terminals 5 and 6 are shorted on starter. That is UTS (up to speed). That will cause the controller to fault out and remove the 120Vac also. I have repaired them in the field many times.
PHP: 8.3.35 Page Time: 0.050s Queries: 22 (0.009s) Memory: 3.0111 MB (Peak: 3.5923 MB) Data Comp: Off Server Time: 2026-10-11 02:51:45 UTC