The elevator wants to take off at high speed prior to the doors closing. Recently changed the tank unit with new valve / motor and pump. This project is new to us. Previous contractor was terminated. When we arrived on site we found it with a seized submersible pump and shorted motor. Not knowing until after we had installed the new components. That the elevator ran up the hoist way on onto the stop ring and the motor kept running for 4 to 6 hrs until contractor arrived on site to turn the main power off. Armor 4C door operator with PM switches and Vanes. Wye Delta Starter. When it is parked on either LU or LD on top of car inspection and you switch it to Auto... It levels down and door opens and just as the car door starts to close the car takes off at high speed in the up direction. PM switches check out good. Top and bottom directional switches check good.... It's a weird one. Changed a number or 110 VDC relays in the controller. Help!

Joined: Aug 2011
Posts: 563
U
addict
addict
U Offline
Joined: Aug 2011
Posts: 563
First thing I would do is find out why the car runs with the doors open ie shorts on locks, wiring etc. That's scary. As to the speed, I would change the star/delta change over to a slower time so at least you know its not going to fly rom the landing. Then adjust to suit. I would also find out why there is no/faulty run timer.

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
up contactor welded? pull coil wire on up wye contactor.then what happens. Trouble shooting 101.

Joined: Mar 2014
Posts: 68
journeyman
journeyman
Joined: Mar 2014
Posts: 68
Will the car run down with the doors open like it does in the up direction?

Joined: Jan 2010
Posts: 671
D
addict
addict
D Offline
Joined: Jan 2010
Posts: 671
Is the valve sized correctly. Are the up and high speed relays picking? Are there capacitors across these contacts shorted? We need a little more info to help you out.

Joined: Oct 2012
Posts: 15
R
stranger
stranger
R Offline
Joined: Oct 2012
Posts: 15
Only in the up direction.

Joined: Aug 2011
Posts: 563
U
addict
addict
U Offline
Joined: Aug 2011
Posts: 563
Originally Posted By: rompkinron
Only in the up direction.

You shouldn't be getting a go signal to the up and star contactor until after the doors close. Check you door circuit in the up direction for a short.

Last edited by uppo72; 12/10/15 12:02 AM.
Joined: Jan 2010
Posts: 671
D
addict
addict
D Offline
Joined: Jan 2010
Posts: 671
Ill ask again in the valve sized right. I have seen elevators start running up as soon as Y comes in when someone has turned Bypass instead or relief. If your valve is sized correctly then it a matter of trouble shooting and find out why Up and high speed are picking before doors and gates are closed. If it only does it in one direction then your problem lies on the up side of the circuit.

Joined: Aug 2011
Posts: 29
B
newbie
newbie
B Offline
Joined: Aug 2011
Posts: 29
^^^ couldn't agree more, I too have also seen that.

Joined: Aug 2011
Posts: 563
U
addict
addict
U Offline
Joined: Aug 2011
Posts: 563
Originally Posted By: danzeitz
Ill ask again in the valve sized right. I have seen elevators start running up as soon as Y comes in when someone has turned Bypass instead or relief. If your valve is sized correctly then it a matter of trouble shooting and find out why Up and high speed are picking before doors and gates are closed. If it only does it in one direction then your problem lies on the up side of the circuit.

I take it you mean even the bypass pressure is good enough to push oil to ram and lift the elevator? My problem with that is, the Y shouldn't even be engaging until the doors shut. The motor shouldn't be attempting anything at that point.

Last edited by uppo72; 12/12/15 12:23 AM.

Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.021s Queries: 34 (0.007s) Memory: 3.0437 MB (Peak: 3.5923 MB) Data Comp: Off Server Time: 2026-09-20 18:22:35 UTC
Valid HTML 5 and Valid CSS