Hi, i have a Kone Monospace kdl16l which gives error code F1-0126 . F2-0026 . sub code 1046-0-0 . does anyone know what it could be ... ? the elevator is on the ground floor and can not be called before taking power off and on again , the run fine for a few hours until it is the same error . the error will never while driving.
hope someone can help me.... blush
0026 is Fault from drive system. perhaps a thermistor is getting too hot if it's happening every few hrs.
An 0126 error can be caused by a door lock contact, or a short duration break in the Safety circuit.
Hello
The Fault Code:
126 1046 Automatic brake test
Automatic brake test has failed too
many times. 0 0
Problem with brakes. This fault occurs if there's too many consecutive
126_2071 or 126_2072 faults.
Drive is faulted. By user: switch to inspection/RDF
mode.
Many thanks for the quick reply,
I think you are right that it might have something to do with brake test
I adjusted the brakes and there should be no problem, does anyone know what fault in the brake test may come from...?
Is it a defect drive module or is it somewhere else..?
Can it have anything to do with the temp. in the shaft, maybe its to cold?
The shaft temp. does never go below 0 degrees celsius.
Do you know if the fault codes for a v3f16l drive, is the same at a kdl16l drive?
Thanks in advance.
The brakes we test the floor made, and is aimed at brake gap is too large or poorly goes, comes the error 0126th
The braking gap is 0.005-0.01.
What software is on the KDL16 !!
The drive is: KDL16L/12A, type KM953503G625, rev 1.3, S/N 103AO10310043.
Sorry!
The software query the KDL-Drive is in menu 6.97. (1.10; 1.24; 2.24;...)
Best regards
PHP: 8.3.36 Page Time: 0.029s Queries: 30 (0.009s) Memory: 3.0322 MB (Peak: 3.5926 MB) Data Comp: Off Server Time: 2026-11-05 18:41:05 UTC
