Hey guys, I'm getting a constant lowbatPEBO fault every day or so on this MX GC.
Ive replaced the batteries and have done multiple resets.
Any help on how to disable / remove this fault?
Thanks.
|
|
|
|
|
Joined: Aug 2014
Posts: 134
member
|
|
member
Joined: Aug 2014
Posts: 134 |
Change the battery for the emergency rescue operation.
|
|
|
|
|
Joined: Jun 2018
Posts: 13
stranger
|
|
stranger
Joined: Jun 2018
Posts: 13 |
Hi there, i have same issue , any solution please?
"heisenberg" did you manage to solve the problem?
BR.
|
|
|
|
|
Joined: Jun 2018
Posts: 13
stranger
|
|
stranger
Joined: Jun 2018
Posts: 13 |
I forgot to say that i measured the baterries on PEBO rescue device, there are 4 batteries , 3 are in referent values from12.2V - 13.1V, but 1 was 9.7 V. so i replaced that one and had lift working for one week. But after one week the lift stoped with same error "batlowPEBO", so i measured the new battery i replaced a week ago, and the result was 10.1 V i think the issue is with battery charging.
|
|
|
|
|
Joined: Jun 2018
Posts: 13
stranger
|
|
stranger
Joined: Jun 2018
Posts: 13 |
Solved the issue with adding additional stand alone battery charger directly to battery which does not charge, and everything works for more than 3 weeks.
|
|
|
|
|
Joined: Apr 2014
Posts: 280
Engineer
|
|
Engineer
Joined: Apr 2014
Posts: 280 |
Basically on my unit there is a UPS device in the headroom of the lift shaft, it charges two 12v batteries wired in series
The UPS has an internal dry relay contact that closes when the UPS internal battery is good, however when the battery in it becomes faulty, the contact will open.
When the contact is open, the ASIXB main board IO plug pins number 1 and 4 are no longer connected, giving the pebobatlow fault.
If you follow your electrical schematics correctly, you'll see that io.1 is 24vdc output and io.4 is your pebobatlow signal, when it's not receiving 24vdc, you'll have the pebobatlow fault.
Either your AXISB board is not giving out 24vdc correctly, your NGL power supply is too low or your UPS is not closing the required contact.
|
|
|
|
|
Joined: Jun 2018
Posts: 13
stranger
|
|
stranger
Joined: Jun 2018
Posts: 13 |
Well , thank you "heisenberg" this is nice explanation, as i have no experience with schindler your post is very useful for me. Cheers mate 
|
|
|
|
|
Joined: Apr 2014
Posts: 280
Engineer
|
|
Engineer
Joined: Apr 2014
Posts: 280 |
|
|
|
|
|
Joined: Jun 2018
Posts: 13
stranger
|
|
stranger
Joined: Jun 2018
Posts: 13 |
Basically on my unit there is a UPS device in the headroom of the lift shaft, it charges two 12v batteries wired in series
The UPS has an internal dry relay contact that closes when the UPS internal battery is good, however when the battery in it becomes faulty, the contact will open.
When the contact is open, the ASIXB main board IO plug pins number 1 and 4 are no longer connected, giving the pebobatlow fault.
If you follow your electrical schematics correctly, you'll see that io.1 is 24vdc output and io.4 is your pebobatlow signal, when it's not receiving 24vdc, you'll have the pebobatlow fault.
Either your AXISB board is not giving out 24vdc correctly, your NGL power supply is too low or your UPS is not closing the required contact. Hello Heisenberg need your assistance, any chance to overbridge the "Pebobatlow" and how? i am attaching the axisb boards photo , and 2 pages of schematics . https://ibb.co/y5PWMLNhttps://ibb.co/HnPpbbzhttps://ibb.co/wgBzqXhBR.
|
|
|
|
|
Joined: Apr 2014
Posts: 280
Engineer
|
|
Engineer
Joined: Apr 2014
Posts: 280 |
You're shorting those contacts and still getting pebobatlow error?
I had this fault before, there was a fault on the GCIOCF board (the board with the reset button)
My board was physically damaged
Pebobat fault would not clear! Super frustrating
Once I got a new board, the fault went away.
|
|
|
|
|
Joined: Jun 2018
Posts: 13
stranger
|
|
stranger
Joined: Jun 2018
Posts: 13 |
You're shorting those contacts and still getting pebobatlow error?
I had this fault before, there was a fault on the GCIOCF board (the board with the reset button)
My board was physically damaged
Pebobat fault would not clear! Super frustrating
Once I got a new board, the fault went away. Yes pebobatlow frustrates me for 2 days, damn battery charger does not charge bateries. attaching photo of pebo device. https://ibb.co/3Cq9Kvh
|
|
|
|
|
|
|
|
|
HW PM
by Chris, January 13
|
|
|
|
|
|
|
|
|
|