#17418 07/01/16 03:57 AM
Can anyone help me with the description of extra info 0x0003000f with a 1209 fault, would be a great help.
1209 Missing Node
________________________________________
Examples:
10010002: LON channel 1, Node type=01, ID=02. (LONIO, dipswitch=02. See list below for p-type)
10030004: LON channel 1, Node type=03, ID=04. (LFT-DPI, dipswitch=04.)
Meaning of values for "p_type":
Value / software name / board names
000(hex) / 0(dec): UNDEF should never occur
001(hex) / 1(dec): GENERIC_IO_BOARD LONIOS16, LONIOH16, ICE, (H)TIC
002(hex) / 2(dec): ARRIVAL_INDICATOR LONDAG
003(hex) / 3(dec): DIGITAL_POSITION_INDICATOR LFTSDPI8, LFTDPI50
004(hex) / 4(dec): LMS_MODUL LONLMS
005(hex) / 5(dec): MACHINE_MODUL not used
006(hex) / 6(dec): CIOHNA Cab IO for HX system
007(hex) / 7(dec): HPBHNA Hall node for HX system
008(hex) / 8(dec): M10_TERMINAL ZRTL
009(hex) / 9(dec): M10_DESTINATION_INDICATOR AZRC
00A(hex) / 10(dec): M10_SPEECH ANN
00C(hex) / 12(dec): MX_COP LONCOP, LONCPI
00D(hex) / 13(dec): MX_LOP LONCUS, LONIO(C), LOND(G)I
00E(hex) / 14(dec): MX_OPT_LIP_BIG LONCUB, LON(P/D)GIO, LONDY(H/IO), LONPII
01E(hex) / 30(dec): MX_LONIC LONIC, LONGIC
036(hex) / 54(dec): CAR_DOOR_NODE LONIBV, LONDIM, LONV70, PLDA
037(hex) / 55(dec): SHAFT_DOOR_NODE not used
03C(hex) / 60(dec): HIOMRLPP HIOMRL plug and play for NA
064(hex) / 100(dec): LOCAL_IO_BOARD ASILOG(A), ASIX(A)
Source ID None.
Causes and Actions ID Possible causes of message Actions to be taken
1 No power at fixture or I/O board Check power LED's and power wiring.
2 Damaged or defective fixture or I/O board Replace damaged fixture or I/O board and repeat LON freeze command if necessary.
NOTIME #17426 07/03/16 03:50 PM
Do you know if this board under the CPU is interchangeable with another Car, trying to Chase down 10 flt and now 7 flt
Points to
PIOVECL Q3
this is a Small comunication Board
Question 1 Car STOP ?
because look like a PI board is fault
but true cueldbe other
fallow the Yellow Shield Wire inside controller and true the Cab.
NOTIME #17430 07/05/16 08:46 PM
Other yellow inside the controller?
True the Cab?
Yellow Schield wire connect all LON board
NOTIME #17440 07/07/16 10:39 PM
OK, thank you..
Do you by chance know what Flt 148 is?
0148 Safety T4
Used for the monitoring of the landing door contacts KTS. The safety circuit is open before the fourth tap (ISKT4) but after the third tap (ISKT3). The message is logged if:
a) the safety circuit opens during a trip due to a landing door contact (any) which opens unexpectedly.
b) the safety circuit does not close as expected after the door has closed.
Comments: Downward safety circuit tap input (ISKT5) will not create corresponding error message. Refer also to wiring diagram for contacts causing the error.
If this error persists increase the value of the drive parameter 'DOOR_CONTACT-DELAY' to 50 (corresponds to 0.5 s), 70 or 100. This is time the logic waits during startup from the first time the SKD signal 5 (safety end) is received to the moment when the door overbridging is disabled. During this time, the door contacts may bounce. Do not increase the value for this parameter too much because it will further increase the trip preparation timer. More care should be taken to improve the adjustment of the door movement.
NOTIME #17457 07/09/16 04:10 PM
Thank you Very much!
PHP: 8.3.33 Page Time: 0.034s Queries: 32 (0.011s) Memory: 3.0373 MB (Peak: 3.5924 MB) Data Comp: Off Server Time: 2026-09-21 03:37:11 UTC