Hi Everybody

I would appreciate if someone could enlighten me on these points:

(i)The Regen Drive use the same power cable from the Distribution Board to import power during lift operation and export power during regeneration.

I can't understand how fast the regen drive synchronise with the utilities power? Does it synchronise?

(ii) If during lift moving downward and regeneration, there is a power cut, the power will go to the utility grid. Is this right or there is a safety.

(iii) If there is no load on the distribution board busbar during regeneration, will the power go to the grid? Is it appropriate? If the meter is not bidirectional, what will happaen?

(iv) Does someone could share a document on the principle of operation of the OTIS Regen Drive?

I'm new to this technology and confused. Any other helpful information would be most welcome.

Thanking everyone in advance.

Joined: Mar 2015
Posts: 49
I
newbie
newbie
I Offline
Joined: Mar 2015
Posts: 49
1. Yes, same wires for drawing power and feeding back into the building.
The regen drive must be phased correctly to operate. This is accomplished at installation. This is probably what you mean by "synchronize"

2. If a heavily loaded elevator is moving down, or an empty or lightly loaded elevator is moving up the regen drive is producing power. However, if the power goes out when the elevator regen system is producing power, the elevator will quickly stop due to the loss of power and the brake setting. The motor will not be spinning anymore so no more regen.

3. In most regen situations, the electrical load will be distributed locally, and the power meter will just slow down. If the only load is the elevator operating in regen mode, power will go to the electrical utility grid. If the building meter does not have the capability to turn backward, power will still go to the grid, but the building will not reap any cost benefit. This scenario would be a very rare occurrence anyway.

4. Here is a good link to the info you want:

http://www.elevatorbooks.com/Content/Site125/FilesSamples/179592pdf_00000088467.pdf

Joined: Mar 2017
Posts: 3
L
stranger
stranger
L Offline
Joined: Mar 2017
Posts: 3
Thank you very much to share the knowledge.

Joined: Mar 2017
Posts: 3
L
stranger
stranger
L Offline
Joined: Mar 2017
Posts: 3
With respect to phased properly as you mentioned, Does the Regen Drive prior to feed the building busbar, have to ensure during each regeneration that the voltage with respect to the Grid Voltage are
(i) same phase rotation
(ii) same voltage magnitude
(iii) same frequency
(iv) same phase angle

Thanks

Joined: Mar 2015
Posts: 49
I
newbie
newbie
I Offline
Joined: Mar 2015
Posts: 49
Yes, the regen drive is designed to ensure that the voltage, frequency, and phase are all within a certain tolerance.


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.019s Queries: 24 (0.005s) Memory: 3.0162 MB (Peak: 3.5918 MB) Data Comp: Off Server Time: 2026-09-20 13:29:02 UTC
Valid HTML 5 and Valid CSS