Joined: Feb 2015
Posts: 26
D
improving the trade
improving the trade
D Offline
Joined: Feb 2015
Posts: 26
I have a Tac 20 and I am learning how to use the IMS. The elevator sits with the doors open and I have a B-44 status on one of the screens. My fault log seems to be locked up, meaning I can not seem to get new faults to replace the current faults. (1073,1041,1098). looking for some ideas on the B-44 and why my faults are locked.

Joined: Jan 2014
Posts: 736
R
old hand
old hand
R Offline
Joined: Jan 2014
Posts: 736
With the car highlighted in network under service menu, open Remote Fast. In the box that opens type RFL to clear the faults. From your faults it looks like you have a door open limit problem or some other door problem. If you open the Remote Fast with the group highlighted it will only clear Group Faults. Not sure where you got your IMS but you also need good help files to steer you to the errors. Also an IMS User Guide is helpful.

Joined: Feb 2015
Posts: 26
D
improving the trade
improving the trade
D Offline
Joined: Feb 2015
Posts: 26
Dear Rolly

I will swing by this week and try clearing the faults and see what pops up new. any ideas on the B-44?

Joined: Dec 2010
Posts: 639
Likes: 4
E
addict
addict
E Offline
Joined: Dec 2010
Posts: 639
Likes: 4
I believe on the TAC20, the CPU has to see gate lock, door lock and DCL in that sequential order without much delay between the last two inputs. Conversely, it must see them in reverse order during open cycle. Sometimes it's a timing issue between the the last two making the trouble intermittent.

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
The 1098 is usually a bad N/C contact on the HDIF contractor or bobbling door locks. Your B-44 status is from the 1073, door lock monitoring. If DOL goes high while hall or gate locks are made, the CPU thinks there is a jumper left on a door lock. That fault of seeing DOL when it shouldn't and a 1041 that says it did not get to DOL in the allotted time makes me suspect a communication problem with the door board. Open your door diagnostics window and see if there are any faults at the bottom. Also, if you open door smart fast and the table doesn't populate, you don't have communication with the door board.

Joined: May 2011
Posts: 487
E
addict
addict
E Offline
Joined: May 2011
Posts: 487
Parallel the HDIF and CDCF relay contacts.

Last edited by E-man; 04/24/17 02:17 AM.
Joined: Feb 2015
Posts: 26
D
improving the trade
improving the trade
D Offline
Joined: Feb 2015
Posts: 26
all very good replies. I need to get back to the site and test some these theories and let everyone know the outcome. thanks


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.025s Queries: 28 (0.008s) Memory: 3.0284 MB (Peak: 3.5931 MB) Data Comp: Off Server Time: 2026-09-21 05:40:54 UTC
Valid HTML 5 and Valid CSS