0 members (), 14 guests, and 3 robots.
#21163 07/18/17 03:40 PM
Getting a "Incoming Power Low Line" on the screen. Fault contactor pulls in, then we get that message and it drops out. All legs are reading 480-483 volts. Reading 120v between 1 & 3 on the starter. Waiting on a call back from Siemens but my guess is bad starter?
Or logic board......
That would be my guess too. Not sure if the logic board does the voltage measurement but I'm thinking not.
Did you measure voltage with a meter or use the Status Menu on the starter? The menu on the starter will tell you what the starter is seeing. If it differs from your meter, something is wrong with your starter. I don't think you can adjust the low voltage clamp on those starters.
It was the logic board. I just haven't ever seen that fault before.
PHP: 8.3.33 Page Time: 0.022s Queries: 24 (0.006s) Memory: 3.0153 MB (Peak: 3.5929 MB) Data Comp: Off Server Time: 2026-09-21 16:04:37 UTC