Posts: 52 |
Book says not getting hall lock, car gate or door close limit, i know i have all 3. Replaced door board, any thoughts? Not very familiar with these units. Thanks
Posts: 805 |
If the computer see's a gate contact, or a door contact, you have to make the close limit inside of 4 seconds. Or if it see's a close limit you have 4 seconds to make up the other two. If not you get a door re-open.
Posts: 52 |
I see them come up in the controller but doors just cycle. I would think i would get a 44 fault more often but i have only seen that once. Doors just keep cycling
Posts: 805 |
Are you picking K7 relay? that looks at safety string, door and gate locks and the door close limit.
Posts: 805 |
BTW, the close limit is achieved through door motor encoder counts.
Posts: 270 Likes: 2
Posts: 270 Likes: 2 |
Isnt it the senor with the magnet on the clutch?
Elevator Guy
Elevator Guy
Posts: 22 |
Yes close limit is a magnet on clutch. Sensor or bottom of door board mount 46 normally is a door lock when you look at the fault the LEDs will match fault code. You can see if exactly what made and what didn't . Almost it is only as smart as what I/o it sees or where voltage was lost.