#22064 10/31/17 07:28 PM
Shootintrouble
Shootintrouble
Need some help here fellas. Can you communicate with a swift 5000 via hyperterminal and if so whats the proper procedure? Thanks.
old hand
old hand
Yes, 1200, 8, N, 1.
Shootintrouble
Shootintrouble
Got a 5000 tripping out with a 23, 24 flt only in the down direction, different spots in the h/w. Travel demand is 500fpm actual 497. DAR, REG Boards have been replaced with boards from running car in the same group. TAC & TAC cable have been replaced. Pwr supplies good with no AC ripple.Any ideas?
old hand
old hand
which fault comes first?
Shootintrouble
Shootintrouble
Magnetek drive? How close is your tach cable conduit run to high voltage wires? Are there big ass radio,microwave, cell tower, etc stuff on the roof of the machine room?
If all else fails, read the instructions
Shootintrouble
Shootintrouble
MG. I pulled a new tach cable outside of the piping and shortened it as much as I could. No tower interferences.
old hand
old hand
Check the SCRs
Shootintrouble
Shootintrouble
Got it. I tweaked on the F pot on the DAR board. Been running with no faults for 8 hours. Thanks for all the help.