#22385 12/07/17 09:53 PM
vatorman1997
vatorman1997
I have a Kone KCM831 controller on a job that experienced a power outage and I am now receiving the faults of 82 and 15. I do have the book and it tells me to look at relays 443:1 and 443:2, however, I am not sure where these are located in the controller or car top. Can anyone point me to them? Also, to where is the ADON board is located?
-Corey
Corey,
The ADON board is below the LCECPU.
This may be your trouble. ADON 1 board is problematic, especially if faulting on 82 & 15. You might have to upgrade to ADON 2.
One difference between 1&2 boards is the location of X6&5 connectors. The 1 board has the plug locations at the bottom of the board. The newer board has the two connectors at the upper center, and a series of LEDs in roughly two columns under X5&6 connections.
Hopefully your book show the replacement procedure.
Relays K443:1 & 2 are top left on the ADON bd., they are soldered on.
vatorman1997
vatorman1997
Thanks for the help. I will try changing that board out.
-Corey
Make sure you have the ADON 2 write up before you start.
vatorman1997
vatorman1997
Thanks for the help everyone. The ADON board was the fix.
- Corey
Thanks for closing this one out!
Have a Merry Christmas.
An expensive fix at that......... (for non-KONE customers).
PHP: 8.3.33 Page Time: 0.026s Queries: 28 (0.006s) Memory: 3.0264 MB (Peak: 3.5925 MB) Data Comp: Off Server Time: 2026-09-21 09:23:57 UTC
