I have a problem with MCS 120 Hydraulic with Bucher valve. The lift very often has a problem with fault log DBSS only with status fault on Otis tool DAR ST. Whenever has an error the call is not registered and will working Normal again after we reset the power supply OFF and ON. We have changed the Bucher selenoid, the new LCB2 board. PSR switches, whole the contactors including LV1, LV2, and LVC.
Does the lift have a pawl device? If yes, try to disable the Anti Creep Device for testing purpose. Set parameter in LCB-II M1-3-1-4 (Drive parameters) ACD/UXT = 0 (Disabled).
It looks like the only things that can generate the DAR state is:
- Fault from the Bucher control (Is the relay on the Bucher Power Supply connected?, If yes try to bridge this relay). - Or one of these inputs have been active: OTS (Oil Temp Switch), PLS (Pressure Limit Switch), MPD (Motor Protection Device), THB (Thermo Contact).
I have not checked yet about the 0 value of Bucher Valve, could you advise me how to check this, please I have checked the 0 value on parameter LCB_2 only. the controller of the Bucher is Delcon Controller.
dear heisenberg, normally relevelling is working very well and many times tested. After hours, releveling may not occur due to cold oil or a valfe fail? So if I set parking floor for a diffrent floor samething may happen? But I tried floor changing to test. As you say I set the parking floor "ARD-P and ARD-T". but controller malfunctioning. car goes for parking floor (screen turns ARD from IDL). then goes bottom floor (Service tool's screen shows PRK). again and again this keeps on. so I closed these parameters.
Is there a tank heater? Or does this run the motor to heat the oil? If it runs the motor to heat, make sure the valve isn't moving the car when it is heating.
I would certainly put a tank heater in, you have tried everything else. A cheap workaround, just to see if oil temp is the issue is to put a heat lamp on the valve. It may give you an idea. Just a thought.