Greetings, thanks for reading any advice is greatly appreciated.

We're working on 2 hydros for a train station (new construction), eastbound and westbound.

Westbound lift has a noticable vibration on startup, no vibration going down.

Eastbound lift is running smoothly.

The only difference between the two elevators is the length of the hydraulic piping. Eastbound is around 20' and Westbound is around 65'.

Could the length of the pipe be the cause of the vibration?

Thanks
-Dennis

[Linked Image]

Last edited by DennisPEC; 06/04/18 02:13 PM.
Joined: Mar 2016
Posts: 270
Likes: 2
L
Elevator guy
Elevator guy
L Offline
Joined: Mar 2016
Posts: 270
Likes: 2
Could be air in the lines,plugged intake on the power unit,if its telescopic a piston could be hung up,most likely not the length in oil line unless its not secured

Joined: Dec 2010
Posts: 639
Likes: 4
E
addict
addict
E Offline
Joined: Dec 2010
Posts: 639
Likes: 4
Could be pipe run length, but vibrates only in the up.

Isolation around feedline that penetrates floor or walls;
How does the motor/pump sound in the machine room?
Isolation at the piston to car? Isolation coupling in the feedline and a muffler?
Jammed feedline connection transmitting that harmonic pump vibe?

Is the ride spongy at all? Bouncing at slowdown points or final stops?

Joined: Mar 2014
Posts: 215
S
enthusiast
enthusiast
S Offline
Joined: Mar 2014
Posts: 215
I notice they are belt drive. I had a bad sheave on a belt drive once that was out of balance. Replaced the sheave and it was gone. Try pulling the valves after starting the unit up, think low oil test, and see if vibration still exists with no oil going through the lines. If it's still there you have isolated it to the machine room at the very least.

Joined: Dec 2010
Posts: 639
Likes: 4
E
addict
addict
E Offline
Joined: Dec 2010
Posts: 639
Likes: 4
Well, I suppose the OP is still working on his unit issue. It’ll be nice to hear what the outcome was.

Joined: Jun 2018
Posts: 7
D
stranger
stranger
D Offline
Joined: Jun 2018
Posts: 7
Hello everybody,

I'm sorry for not responding, I was sent to a different location.

But I'm back and we are currently doing an inspection on said elevator.

The inspector noted the vibration problem, it has to be fixed.

Everybody, thank you for your responses, they will all be taken into consideration while we try to fix the problem.

I will keep you updated. Thanks again


Here are some more details:
Jack is not telescopic
Air was drained
Line is not isolated
Motor in machine room sounds perfectly fine
Isolation coupling yes, muffler no
Ride is not spongy/bouncy
I checked the belt, everything looks perfect
We did low oil test, no change

Last edited by DennisPEC; 06/14/18 03:54 PM.
Joined: Dec 2017
Posts: 37
H
newbie
newbie
H Offline
Joined: Dec 2017
Posts: 37
Noticed you said no muffler. I would start there.

Joined: Jun 2018
Posts: 7
D
stranger
stranger
D Offline
Joined: Jun 2018
Posts: 7
My mistake, the muffler was preinstalled by Canton.

We opened the drop ceiling and checked the pipe for vibration, there was none. The problem isn't with the length of line.

Joined: Dec 2010
Posts: 639
Likes: 4
E
addict
addict
E Offline
Joined: Dec 2010
Posts: 639
Likes: 4
Thanks for getting back Dennis,

Seems you’ve eliminated several possibilities, and NO PIPE VIBRATION. Did you check for piston to car isolation? Could it be the jack packing, or is down direction smooth in all transitions?
Poster “lowoil” suggested a clog at the pump intake...all ok there?

Joined: Jan 2010
Posts: 671
D
addict
addict
D Offline
Joined: Jan 2010
Posts: 671
Are the mufflers the air up kind? You must air these up as it make a HUGE difference. Also you must air them up with no pressure on the system so manual lower the cars on the spring first.

Joined: Jun 2018
Posts: 7
D
stranger
stranger
D Offline
Joined: Jun 2018
Posts: 7
Hello,

Here's an update.

There is piston to car isolation, it's unlikely that the problem is with the jack.

No vibration from motor room and it's a new installation, clog doesn't seem likely.

The mufflers are not the air up kind.

Somebody from my shop who specializes in hydros came to take a look and the solution was to install a second muffler. But an MTA inspector came and shut that down, he said the long island railroad doesnt want any extra parts on a new build.

I'll keep you posted
Thanks again for the replies

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
I would think that there is air in the jack. did you try bleeding it in the pit at the jack head?

Joined: Feb 2013
Posts: 800
J
old hand
old hand
J Offline
Joined: Feb 2013
Posts: 800
One other thing to try is to salve the piston with that green goop to eliminate the packing.

Joined: Jan 2012
Posts: 37
E
newbie
newbie
E Offline
Joined: Jan 2012
Posts: 37
Does this unit have slide guides and are the rails tight at the bottom landing? Does it have a soft start and is the valve picking before the motor is up to speed? Have you tried adding Cat oil additive?

Last edited by Elevator_Steve; 06/23/18 01:32 AM.
Joined: Dec 2010
Posts: 639
Likes: 4
E
addict
addict
E Offline
Joined: Dec 2010
Posts: 639
Likes: 4
Bummer about the muffler thing, but you’d never know it was the solution till you tried. Swap out the pump (even if it sounds ok) since the vibration is only in the up, nothing to loose there, and at least “you’re not adding parts”.

I’m anxious to hear the fix on this one.

Joined: May 2012
Posts: 194
L
Len Offline
member
member
L Offline
Joined: May 2012
Posts: 194
....I had a unit that did the same thing after we changed packing tried adjust the valve the problem was in the tank unit after the pump and motor assembly was changed out..no more vibration...rides smooth..

Joined: Oct 2014
Posts: 30
C
newbie
newbie
C Offline
Joined: Oct 2014
Posts: 30
I see you have a dry pump on this installation. It may seem like a simple thing but I've seen belts that are not tight enough feel like vibration in the car. The belts skip at a high rate and cause the pump to pulse. Did you confirm the belts are nice and tight?

S

Joined: Jan 2014
Posts: 736
R
old hand
old hand
R Offline
Joined: Jan 2014
Posts: 736
And they have to be tighter then Banjo strings.

Joined: Jun 2018
Posts: 7
D
stranger
stranger
D Offline
Joined: Jun 2018
Posts: 7
Hey everyone,

Quick update: We were approved to install the second muffler, it's the air up kind this time. Fingers crossed.

[Linked Image]

Joined: Oct 2014
Posts: 30
C
newbie
newbie
C Offline
Joined: Oct 2014
Posts: 30
Hi Dennis,

I don't know if you've worked with those mufflers before, but it might be hard to get it up to pressure in the air bladder, most air compressors don't build enough pressure. If you have access to a tank of nitrogen it is the easiest way to do it.

S

Page 1 of 2 1 2

Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.137s Queries: 55 (0.102s) Memory: 3.1163 MB (Peak: 3.5929 MB) Data Comp: Off Server Time: 2026-09-20 19:20:42 UTC
Valid HTML 5 and Valid CSS