My team is in the process of modding a 6 car group of Montgomery Miprom 2 elevators, I was hoping someone here could help me get a hold of a manual or at the least a nomenclature for the miprom 2 Dispatcher and its signals. Any and all help is greatly appreciated. Work safe
This is the common panel for a group of Montgomery elevators. Usually these were for earlier analog drive units. They were a parallel hall calls, and not a series dispatched group. As were Miprom 21"s. The common panel had the Fire service, Hall calls, etc;
John: Common & dispatcher are considered the same, correct? I suppose the main concern at this point is if these signals are low voltage (15-5vdc) or high (120vac). We are trying to integrate our dispatcher to the old miprom so they still dispatch together. I think we may have found a way, but i will update if anyone is curious
If the red hall call inputs are high, you have Bi Logic controls. You put a call in by grounding the input. If the inputs are low you put calls in with 120vac to the input. In later years they had a 24vdc input system. But I believe yours is either 120vac, or Bi-logic. As for the dispatch question, the Miprom 21 used the first two cars in the group as serial communication dispatchers. In the older analog drive era, they used the common panel, and parallel communication to answer hall calls.