0 members (), 58 guests, and 3 robots.
Schindler ER0094 block error keeps coming replaced the SDOOR AND CDOOR RELAYS changed all the door locks and gate switch still comes up any suggestions
The controller is a 330A
Keep the tracks very clean and the ramp lubed up well.
20 yr tech
20 yr tech
94 Error FATL. Only resets by turning lift off while on inspection. Once rebooted, turn off inspection. Should be gone. If it comes back you need to read the sub menu error code. In the fault log. That number will tell you which area to look at. There are Litterally 99 reasons why you are getting a 94 code.
Fixed the 94 block issues now getting a 20- position lost fault - extra 0x00000067 do not see this fault in the manual has anyone experienced this if so can you help out?
If Im not mistaken that is re leveling failed. The car didnt move quick enough. Check the bypass setting if its taking too long to move and it goes to re level it will send out that fault.
IUEC48
IUEC48
Check R176. Bottom left of the main board. It's likely cooked.
PHP: 8.3.36 Page Time: 0.028s Queries: 28 (0.009s) Memory: 3.0273 MB (Peak: 3.5928 MB) Data Comp: Off Server Time: 2026-11-05 07:18:55 UTC