Anyone help on this fault?
TAC 32 MRL Hydro
Getting fault
1859 Discrete SPI HW failure - A CPU/IOF hardware failure.•
Check F1 on the IOF Card. • Reload generic and job software.• Replace the IOF Card.
Car won’t take calls, no power to doors. Will not run on inspect.
All fuses are good. I know fault says IOF. I’m pretty sure that’s older nomenclature and is now called the IOD. I could be wrong. Is the IOD board shot ? I assume it is. But would like a second or third opinion before I buy one.
Thanks
spittman
Posts: 270 Likes: 2
Elevator guy
Elevator guy
Posts: 270 Likes: 2 |
Cpu is bad,had this fault last summer when a duplex took a power blip. Changed both boards just to be safe.
Posts: 44 |
Thanks for the reply lowoil, I suspected that was my problem,. I'll get one ordered and i'll Let you know the outcome. Appreciate the reply.