Posts: 120 |
Schindler 3300, have fault 4305. What is 4305 and how to reset fault?
Thanks.
Posts: 43 |
E_SAFETY_DEVICE_CAR_UNINTENDED_MOVEMENT A elevator safety device has detected that the car has performed a uncontrolled movement (e.g left the door zone with door open). C1:Serious failure at traction means or brake A1:Check carefully reason for unintended car movement and resolve problem. Release elevator from blocked state by dedicated reset of the tripped safety device. C2:Car door safety contact opens at start A2:Verify the correct function of KTC, adjust KTC accordingly. Verify the correct installation of the doors and resolve any issue found.
Engineer
Engineer
Posts: 281 |
To reset ucm fault Hit enter Number 10 will appear Hit enter again, it will change to 101 Hit Up and get to 127, hit enter 127 0 will appear Hit Up to change the 0 to 1 Hit enter Fault should now be cleared
Posts: 120 |
Cool, thanks. I'll check it out Monday and try reset.
Posts: 44 |