0 members (), 31 guests, and 3 robots.
Posts41,073
#31972 10/22/21 02:53 AM
I have a 5 stop kmc831. That will run for a day, week, or month until it generates these faults, and I find it in the overhead. No one is ever occupied, car is always empty. 130 fault occurs 1st however I have a Kone drive so this fault is not used ( according to manual). 108 is position encoder, motor encoder, load weighed, motor wiring, brake stuck….exc. the car slows at terminal floor. Then seems to start again into overhead. I have only seen it happen once. Went through the brakes, checked encoder wheels, etc… any help is appreciated.
does it not write a subcode? what kind of drive and motor are you working on?
Jadam #31989 10/26/21 01:07 AM
108 gets 2009, and 2013. 130 gets nothing 180 is self explanatory.
If you are working on a Kdl drive, 108-2013 the parameter is wrong ore the tarcho is broken.
That fault could also be caused by a loose or broken ground wire in the Tach shielding.
PHP: 8.3.36 Page Time: 0.108s Queries: 24 (0.025s) Memory: 3.0143 MB (Peak: 3.5904 MB) Data Comp: Off Server Time: 2026-11-06 23:38:06 UTC