Engineer
Engineer
Posts: 281 |
Got an issue with a Kone LCE installed in 2018 Showing the fault code 02 63
I can run it on recall from the landing, but it will not take off on normal.
My manual does not go up to 02 63
Posts: 43 |
02 63 20 11 DS Applicable for EN81_20 feature: close end signal is missing for 10seconds when doors are closed with further calls are present. Close end signal is missing for 10seconds when doors are closed with further calls are present. -F0263 is posted in UI. Exsiting calls will be cancelled and no new calls are allowed."OUT OF SERVICE" message is displayed in both car and landing. -For AMD Close end signal is in correct state or by power cycle or Turn ON RDF / Inspection For AMD + Swing Turn ON RDF/ Inspection or Power cycle -Close end signal is disconnected or removed
Engineer
Engineer
Posts: 281 |
Thanks Bojan, I've found that the close end voltage isn't dropping via the door operator optical output
Seems like the amd d15 board is faulty
Posts: 43 |
Welcome,
if you need a new error list, you can contact me
Posts: 11 |
I'm looking for that error list if you have it. Thanks [email protected]
Miami Elevator
Miami Elevator
Posts: 55 |
I might have the Mini Space error list. Will share it here if I found it
Shoemaker
Shoemaker
Posts: 42 |
Hi Does anyone have the error list : LCE FAULT 0254 ??? [email protected] /shoemaker
Kindly Regards
Shoemaker
Posts: 522 Likes: 2
Posts: 522 Likes: 2 |
All my docs only go up to fault 02 39.
Posts: 110 Likes: 1
Posts: 110 Likes: 1 |
02 54 DS Closed end signal is not ON with in 10 sec of door closing .This fault is thrown when the elevator is in Car top / RDF inpsection mode.
I have up to fault 294,
Pm me if you need it.