0 members (), 35 guests, and 3 robots.
#32347 01/11/22 05:23 AM
Engineer
Engineer
Got an issue with a Kone LCE installed in 2018
Showing the fault code 02 63
I can run it on recall from the landing, but it will not take off on normal.
My manual does not go up to 02 63
02 63 20 11 DS Applicable for EN81_20 feature: close end signal is missing for 10seconds when doors
are closed with further calls are present.
Close end signal is missing for 10seconds when doors are closed with
-F0263 is posted in UI.
Exsiting calls will be cancelled and no new calls are
allowed."OUT OF SERVICE" message is displayed in both car
and landing.
-For AMD
Close end signal is in correct state or by power
cycle or Turn ON RDF / Inspection
For AMD + Swing
Turn ON RDF/ Inspection or Power cycle
-Close end signal is disconnected or removed
Engineer
Engineer
Thanks Bojan, I've found that the close end voltage isn't dropping via the door operator optical output
Seems like the amd d15 board is faulty
Welcome,
if you need a new error list, you can contact me
I'm looking for that error list if you have it. Thanks
[email protected]
Miami Elevator
Miami Elevator
I might have the Mini Space error list. Will share it here if I found it
Shoemaker
Shoemaker
Hi
Does anyone have the error list :
LCE FAULT 0254 ???
[email protected]
/shoemaker
Kindly Regards
Shoemaker
All my docs only go up to fault 02 39.
02 54 DS Closed end signal is not ON with in 10 sec of door closing .This fault is thrown when the elevator is in Car top / RDF inpsection mode.
I have up to fault 294,
Pm me if you need it.
PHP: 8.3.36 Page Time: 0.031s Queries: 32 (0.010s) Memory: 3.0339 MB (Peak: 3.5904 MB) Data Comp: Off Server Time: 2026-11-05 14:32:12 UTC
