#33488 07/27/22 01:30 AM
Phase 1 recall doesn’t work, keyswitch flukes out ok. Assuming the LCEHAS board is the issue?
beaupeep #33495 07/27/22 05:40 PM
Yes the switch goes through the HAS board. Verify the fire service parameter to be sure it's functioning
beaupeep #33498 07/27/22 08:46 PM
If I remember right there are a couple parameters that can make that switch not work. Also have had to do a LON download to get it to work. Had a duplex that wouldn’t work until I turned car 1 off and did a LON download in car 2 or the other way around.
beaupeep #33507 07/28/22 03:44 AM
How do you do a lon download?
beaupeep #33509 07/28/22 05:19 AM
Turn RDF (pos.270) ON. Activate lon download by changing value of menu 5-7 from 0 to 1 or 2 and press Select/Accept button.
Menu 5 - 1
beaupeep #33709 08/18/22 10:20 PM
Dirt, you were totally right, parameter wasn’t on, she works now. Now my hoistway access switches do not work at top and bottom floors, is there a parameter for those? Can see my door locks making up when trying to run it up and down but car doesn’t move. Menu 7.1 is set to 3 which is right but 7.70 was set to 0 which we thought was wrong, is there anything else? Can’t believe it’s 2 boards that are gone.
beaupeep #33711 08/19/22 12:25 AM
I’m not sure about that one… in fact, next week I’m going to look at a KCM hydro that access hasn’t worked on for years. I couldn’t figure it out back then and ordered HAS boards. I’m told they’ve been replaced but no change. Maybe someone else out there knows of some quirk that can keep access from working in those things.
Indirtwetrust #33752 08/25/22 10:01 PM
Got access to work, you have to set up parameter 7-1 and than set 7-70 to the amount of floors you have.