If the heat detector/ fire alarm that activates the shunt trip disconnect loses power or gets damaged/ripped off ceiling should the shunt trip activate or should it just send trouble to the fire alarm panel? Can't find anyone that knows this in field.

Joined: Mar 2017
Posts: 176
Likes: 9
A
member
member
A Offline
Joined: Mar 2017
Posts: 176
Likes: 9
The circuit should be monitored by the fire alarm panel and send a trouble warning if the power activating the shut is cut off. The monitoring point of the must be within 6’ of the shunt device. As far as the shunt going off , it by code could be wired either way fail safe or fail secure so to speak, but I’ve never seen anyone wire it where loss of power would kill the elevator. Doing so while code complaint , does not elevate the need for the monitoring circuit. It does however lead to the potential of more entrapments and isn’t good practice. But again I’ve never seen it wired that way, I can’t think of a shunt manufacture for whom it is even an option.

Joined: Mar 2014
Posts: 215
S
enthusiast
enthusiast
S Offline
Joined: Mar 2014
Posts: 215
Nfpa 72 21.4.5 Says loss of voltage to control circuits shall cause a supervisory signal. This intimates that power is always to be available, so circuit is always fail safe hot. When heat detector closes, or fire alarm panel initiates, it need to shunt. Shunt coils by design shunt when power is brought to it, not when it's removed.

NFPA 72 21.4.6 the devices used to initiate shunt shall be monitored for integrity by the fire alarm panel. So if heat detector gets used, or knocked off the wall, panel should read a supervisory closed, or open circuit trouble.


Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.069s Queries: 20 (0.030s) Memory: 3.0047 MB (Peak: 3.5929 MB) Data Comp: Off Server Time: 2026-09-20 19:20:35 UTC
Valid HTML 5 and Valid CSS