#34585 01/20/23 04:00 AM
Joined: Jan 2023
Posts: 11
J
stranger
stranger
J Offline
Joined: Jan 2023
Posts: 11
So im having a soecifice problem on a dover dmc 1 -4 stop hydro with 1 front landing and 3 rear landings. So car runs to all floors and and opens doors but it will not latch a hall call. I can see the Input signal on my FASt screen and there is 24vdc on the terminal strip but when i press a hall call but it does not latch? Any ideas? Theres no lockout switch either and all parameters are good, like i said if i get in the car i can got to any floor no problem. Thanks in advance

Last edited by Jm21; 01/20/23 04:01 AM.
Joined: Aug 2017
Posts: 579
Likes: 6
E
addict
addict
E Offline
Joined: Aug 2017
Posts: 579
Likes: 6
Will it take hall calls if you jump P24G to 1u, 2d/u etc in the controller?

Joined: Mar 2016
Posts: 270
Likes: 2
L
Elevator guy
Elevator guy
L Offline
Joined: Mar 2016
Posts: 270
Likes: 2
Check all the p24 connections in the car station,find what feeds the hall calls to the clc. Probably a ɓad connection somewhere in there.

Joined: Dec 2015
Posts: 1,766
Likes: 11
I
ElevatorPractitioner
ElevatorPractitioner
I Offline
Joined: Dec 2015
Posts: 1,766
Likes: 11
Make sure the valid opening parameters are correct if your software is new enough. You could have the 56-59 set correctly for the car but not the 52-55 for the group.
If the call lights and doesn’t latch but the car still comes I’d say make sure you have P24GS after the toggle switch in the COP.

Joined: Aug 2017
Posts: 579
Likes: 6
E
addict
addict
E Offline
Joined: Aug 2017
Posts: 579
Likes: 6
Originally Posted by lowoil
Check all the p24 connections in the car station,find what feeds the hall calls to the clc. Probably a ɓad connection somewhere in there.


The hall calls should be fed off p24g in the controller. P24g is the group p24. Just had a duplex job where if car one was shut off the top floor hall call quit working for car 2. Found that whoever had originally installed the job fed the top floor hall call from p24 in car ones controller. Of course if it's off, p24 is dead, moved the feed to p24g and now it works no matter which car is on/off.

If hall calls aint working I would start at jumping it in the controller. Takes 5 seconds and you know right away if the problem is in the hatch wiring/buttons if it works or rule all that out if it won't take the call from the controller.

Joined: Jan 2023
Posts: 11
J
stranger
stranger
J Offline
Joined: Jan 2023
Posts: 11
So update... thanks for the help fellas much appreciated but it was much more cynical lol. So for context this is a 4 stop 1 side is only lobby landing other side only goes to 2,3,4
Presumably front door (par. 56 set to 1) is lobby with fire service key switch and presumably rear door (par. 58 set to 14)r serves floors 2,3,4. So all the hall call wires and car call wires were mixed up. Like 4c was on 1c button etc same with hall calls. Now me thinking someone came in messed it all up i go and rewire everything goin by the inputs... example i place 24vdc on 1u, i see 1u hall call input light up so i land the wire. Right ok so then i can get to the right floor from inside the car but still wont latch a call and mind you only registers door faults but everything works instead of hall calls. But heres the kicker the presumed rear door well thats the side with c.o.p and inspection station so i start thinking let me try something. I set par 56 to 14 and par 58 to 1 and swap the j1 jumpers on door card to now make the presumed rear the front and the presumed front the rear, so guess what...latches a call!! Oh but wait fun dont stop there at this point im excited cuz im getting close so i go to hit the lobby hall call and car goes up to 3...i get in the car hit 3 car goes to 2nd floor...so long story short i had to rewire it wrongly , example i had to take the lobby hall call wire and wire it to 3rd floor input so on and so forth and had to put 4c wire on 1st floor car call, 2c wire on 3rd floor call so on andso forth....so basically u hit lobby and 4d hall call i/o lights up on fast tool but goes to where it needs to. Best guess is previous company pur in another jobs software or clc, but luckily it runs now just hope who ever goes behind me doesnt go by the inputs ...lmaoo...what gets is why was it going to the right floors when i wred the car calls correctly but the operators were wrong then when i switch operator jumpers it wouldnt go to the right floor?

Last edited by Jm21; 01/21/23 04:26 AM.

Link Copied to Clipboard
Photo Gallery
service tool laptop
service tool laptop
by dunkdadrunk, February 4
rip orona
rip orona
by epic_ecodisc, January 7
what controller is this?!
what controller is this?!
by Alex_ELMAN, December 4
HW PM
HW PM
by Chris, January 13
PECCO PH5000 Overspeed Governor
PECCO PH5000 Overspeed Governor
by stankap, September 24
Drive sheave
Drive sheave
by jkh, October 10
The best helper.
The best helper.
by Adrian, August 8
Powered by UBB.threads™ PHP Forum Software 8.0.0
(Release build 20240826)
Responsive Width:

PHP: 8.3.33 Page Time: 0.024s Queries: 26 (0.007s) Memory: 3.0216 MB (Peak: 3.5923 MB) Data Comp: Off Server Time: 2026-09-20 23:01:36 UTC
Valid HTML 5 and Valid CSS