Replaced pumping unit. Now when I turn to automatic it immediately gets the low oil timer. I’ve adjusted the pot, replaced the card and card rack Any help in why this might be would be helpful
Upndown76 #35816 08/30/23 10:33 AM
Was the low timer a float switch on the old tank unit?
Code allows for a timer or switch for low oil protection
Upndown76 #35821 08/30/23 04:12 PM
old hand
old hand
Sounds like PT input is high. That is the low oil input.
Upndown76 #35895 09/08/23 12:49 AM
D Offline
did you replace starter with pump unit? Maybe to a soft start?
Upndown76 #35898 09/08/23 06:58 PM
HA on relay board starts the time for low oil
Upndown76 #36007 09/26/23 01:45 AM
My mistake.
UA relay picks and starts run times.
Apologies.
Upndown76 #36079 10/05/23 09:44 PM
Bump for visibility.
I'm in the same situation.
Upndown76 #36099 10/08/23 10:25 PM
My problem ended up being the TUS input. Lost a jumper with the removal of the old power unit.