#36428 12/19/23 06:55 PM
W Online: Content
Having an issue with a TAC22 displaying INIT SHTDWN. 188E Board was sent out for repair due to a bad CST IO. Board came back and CST IO works now, but car won't run. No faults. Car is about 3" above the floor. I have attached pictures of my IO map and my door operator. I think the INIT SHTDWN is being caused by the DOL/DCL/SE IO's. But my door operator appears to have no comms with IMS? It is the old GAL MODL door operator. Can I move IO's on this controller? I have tried injecting DCL and SE but nothing changes. Appreciate any help.
wltr00 #36434 12/19/23 11:17 PM
I
ElevatorPractitioner
I Offline
The door inputs shouldn’t cause an Init shutdown. What are the faults and have you tried a GET command?
wltr00 #36435 12/19/23 11:50 PM
W Online: Content
Have tried a GET command but nothing was returned. Just G1C1. Should I still do a GET/WRT?
There are no faults.
wltr00 #36445 12/20/23 11:07 PM
I
I Offline
Reload the job and generic software
wltr00 #36532 01/08/24 03:41 PM
W Online: Content
Just went back to this job. Still getting INIT SHTDN. Also getting a 1034 and 1090/1091 faults for LON but no LON on a TAC22. Expansion boards appear to be connected properly. Not sure what D12 should be set to on this. It is set to a 1 currently. Still having issues with DOL, DCL and SE also. No prints so difficult to diagnose. Appreciate any help.
wltr00 #36536 01/09/24 12:52 AM
Have you reloaded the software? Like Dirt said?