#36746 02/01/24 09:34 PM
Hi everyone. Hi have a Tac 20 shutting down on 1096 and 1098. My fault list stops at 1086. Anybody know what these are. ?
Jluff #36747 02/01/24 10:11 PM
MX4 Offline
1096
CDCF failure - This fault occurs when CDCF and CDCFM are in the same state.
1098
HDIF failure - This fault occurs when HDIF and HDIFM are in the same state.
Jluff #36748 02/01/24 11:43 PM
So something is wrong with my door locks. ? Or door limits ?
Jluff #36750 02/02/24 01:09 AM
Usually this is from a bad N/C contact on the CDCF contactor for the 1096 and HDIF contactor for the 1098. I always parallel the N/O and N/C contacts on both of these. Sometimes a really flakey gate can cause the1096 and door lock the 1098.
Jluff #36751 02/02/24 01:11 AM
MX4 Offline
I can’t say I’ve seen both faults come on together, it’s saying the door contact. Check your relays and if you replace them make sure you pay attention to voltage bc I believe they are 110VDC…
Random but I don’t understand why it’s a 120VAC and hits a rectifier to make it DC? Why not just use the AC relay like MUTS - obviously engineers are way smarter than I am but I’m sure someone can make it make sense haha
Jluff #36758 02/02/24 11:01 AM
There is only a CDCF contractor. The company before me removed the HDCF contractor when they replaced the 188e. Any time you have a hall door open with car door closed I see both faults. Just getting off the car top on inspection it happens and needs reset
Jluff #36775 02/02/24 11:07 PM
Uh… That has to be fixed
Indirtwetrust #36776 02/02/24 11:14 PM
What do you suggest.
Jluff #36777 02/03/24 01:06 AM
Installing the parts that were removed and wiring it per print. Removing components and re-wiring safety & door lock circuits is kind of a big deal. I’m curious how they wired it to work with just 1 contactor.
Jluff #36778 02/03/24 01:23 AM
They added 2 smaller relays. I will be back next week and copy the info from the print.