I can’t seem to find the setting LSP-NY. The rope gripper doesn’t set during unintended motion test and book says to check that this is set to one. Any help greatly appreciated. Thanks John
John. H #36835 02/10/24 05:26 AM
MX4 Offline
M Offline
M-2-3-7 go on until you see enable lsp type
0 = disabled
1 = disk brake
2 = rope gripper
3 = gov trip solenoid
John. H #36836 02/10/24 06:11 AM
MX4 Offline
M Offline
Looking through some notes now I question my above answer, I DONT have anything for 311 gem but to find that same parameter on other controllers they appear to be the same (311MECS, gen2 etc)
John. H #36837 02/10/24 01:06 PM
They give the gov trip solenoid as an option to activate the governor to provide unintended motion protection? Lord help the folks on those cars. Of all the Otis' I have only roughly 1/2 do the governor solenoids have the oomph to reset the switch (apollo govs). I wouldn't want to trust it to set it in that scenario.