#37055 03/14/24 09:13 PM
Henchmen
Henchmen
I got a hydro TK MRL very temperamental. Got me two entrapments on the same week. I keep getting fault 1040 watchdog closing failure DCL is not closing in the expected time interval. I already checked my gate, switch and door closing limit and my door locks. I even change the base contact locks but the elevator keeps shutting down. Any ideas?
What kind of operator?
Check nudging operation too. Make sure it doesn't happen when someone holds the doors too long
Make sure you’re checking for faults in the door operator from the door IO and faults window. There isn’t a specific controller fault that tells you there’s a fault in the door operator. If the door faults and shuts down you’ll only see watchdog faults in IMS. The door fault will give you something more specific to go on.
Could be a bad door motor?
Henchmen
Henchmen
It's a MIDI-Series Wittur operator. Didn't have the IMS tool on hand yesterday. Will be on-site today for further diagnostics. I did see more faults come in since I got an emergency call last night. Fault 1068(JRS shutdown) and 1095(dual post rack error). I know these MRL are notorious for jack resync problems and they have a timer to resync. I did an FRJ command but I want if there a way for this to happen less frequently.
I had a similar problem last year, the watch dog trips, the door operator kills itself and the doors close because of the spirator, causing a trap, ended up being the door operator motor, there was one bad spot on it, got a new one, hasn’t happened again
Henchmen
Henchmen
sounds exactly like the problem i have it was last thing to rule out but I will change the motor If need be
Do a wjr to see why and how many times. It's syncing. Is it static or dynamic?
Henchmen
Henchmen
It looks like it's pointing more to the direction of replacing one of the dynamic sensors in the top landing.
You can plug your IMS into the door operator while running upon inspection and check your I/Os buy swipe a magnet past the sensor. Sometimes plugging in to the operator can give the car a brain fart and odd faults but it's ok.
Stupid question. So the door faults in the IO/faults, does that fault log clear when you clear the faults through the rfl command in remote fast for the car faults? Or is it self clearing when powers cycled?
It didn’t always but I have noticed it does in some newer software.
Whats the normal way to clear it?
Cycle door power or clear faults from the Command pull-down menu in Door Smart Fast.
PHP: 8.3.33 Page Time: 0.035s Queries: 46 (0.009s) Memory: 3.0693 MB (Peak: 3.5923 MB) Data Comp: Off Server Time: 2026-09-21 17:43:56 UTC