#37352 - 04/27/24 07:30 PM
RCD redundancy fault. MCE
Alto101
Central Florida
HMC 1000 newer version. Troubleshooting this fault has been tricky. RCD redundancy fault. This elevator was shut down for 2 years. This elevator just needed some TLC and an inspection. Nothing was done to the controller or hydro system. Ran great for a month and this fault started.
CD relay has been swapped. Operates as it should. When a call is registered up or down the car will travel slightly then fault, back to normal then fault, intermittently. If the car doesn't make to the landing motor timer faults. Inspection seems to override this this issue. ( maybe it did RCD fault during inspection but definitely not like Normal, I don't recall this comment 100%) one observation: When I first arrived next day after shutting down the car it took several call with no issue. Almost like things got warmed up and the fault started happening and got worse. Door close LED stays on during travel. Safety Circuit LED goes off during travel when RCD fault occurs. CD relay stays picked during travel and goes off when the car door opens as it should.
#37354 - 04/27/24 10:04 PM
Re: RCD redundancy fault. MCE
[Re: Alto101]
Alto101
Central Florida
It was certainly tech supported but all signals seem correct. Relay swap was first suggestion. Craig is usually very helpful but we had no success.
#37381 - 05/01/24 10:27 PM
[Re: Alto101]
Alto101
Central Florida
F1-8 switches. I have read the fault description troubleshooting. The next step is mentioned to replace the ribbon cable. RB20. Certainly give this a try but it seems doubtful to me.
Today I noticed a very distinct pattern. The unit would take calls to all landings, when the door reach fully open the controller would RCD fault. When the door reached fully closed the controller would "cycle test" and take the next call with no faults. same RCD fault at all floors when the door reaches fully open. The lock circuit drops and picks up as it should. CD relay energizes as it should. DCL and DOL signal correctly.
The room is excessively humid and hot with summer approaching (no ventilation). I noticed vapor droplets built up inside the relays. Oddly opening the door and working out some heat and humidity the fault stopped happening for multiple calls (not sure if this was a coincidence or effective, TBD)