Scrapwood99
Scrapwood99
Posts: 90 |
Does a Dover dmc1a have the capability of wiring in a third zone for a flashing hat ? on my prints I only see two zones primary alternate.tia
Posts: 1,769 Likes: 12
Posts: 1,769 Likes: 12 |
Scrapwood99
Scrapwood99
Posts: 90 |
That's what I thought they want to upgrade there fire panel and they have three sprinkler heads todays code requires flash hat probably no way to accomplish this without upgrading controller.thanks for your info
In this situation my AHJ says to make it work if the controller is capable. Otherwise it doesn’t have to.
Posts: 281 Likes: 5
Posts: 281 Likes: 5 |
If you want to get froggy and you have a couple spare travelers you can add a flasher relay and some simple circuitry. But you shouldnt have to add that because it wasn't required when the controller was installed.
Scrapwood99
Scrapwood99
Posts: 90 |
Yes but since they have sprinklers and they intend on keeping them they have to work with todays code
Posts: 281 Likes: 5
Where are you located? Where I am the requirement for stuff like that goes off the code data plate on the elevator. So if it was installed in 1990 at the 1985 asme17.1 code and flashing hat wasn't required then it wouldn't matter what they did to the fire alarm system because it wasn't required for that elevator when it was initially installed. They would only make us change it if we modded the elevator. I would look at your code books in a17.1 section 8.6 I believe is mod/ repair and I can't remember off the top of my head the fire service section
Posts: 522 Likes: 2
Posts: 522 Likes: 2 |
Where I'm at the flashing fire hat is the indicator for a machine room smoke detector trip. A heat detector trips the shunt trip disconnect prior to a sprinkler head blowing.
Scrapwood99
Scrapwood99
Posts: 90 |
But the hat flash wasn’t required for the machine room smoke until 2004 or until Group 4 was adopted for CA.