Posts40,945
#39938 08/09/25 04:22 PM
Bobbybolognie
Bobbybolognie
Working on an old traction unit without as built drawings. Have drawings that are similar so there's missing information. Looking for the door open/close circuit including the motor (on top of the car) control. The door opened and that's where it stopped. Door close timer? Safety circuit holding door open?
Dover C32126
Bobbybolognie
Bobbybolognie
I'd like to see the typical logic (circuit) for the door motor field control Open/close.
How many floors, stand alone or bank?
Bobbybolognie
Bobbybolognie
I’m working on this elevator again. Has doors on both sides. However it get stuck with the door open on the side that only opens at one floor. The DT door open timer is initiated (led on) it times out but immediately goes back to timing. I don’t have accurate prints to troubleshoot the two door circuit. I talked to a guy from downstate NY that works on them a while ago. Trying to find his contact information.
Bobbybolognie
Bobbybolognie
One bank, 4 levels, 3 doors on South side, 1 on North side
Bobbybolognie
Bobbybolognie
SE (SE1) (and SE2) relays are energized. Pull either one out and DT stops timing. So CS (1,2&3) are energized. The print shows as long as CS is on then so is SE.
Bobbybolognie
Bobbybolognie
Working on the Dover Composite Traction Elevator 1970's. I have drawings T2530, T3091 & T2244. Not sure which set is right. Dover's archives weren't readable. I'm looking for the schematic for the shaft doors closed interlocking/latching switches that you use the through hole tool to open the shaft outside door. These switches are located in the top corner of the shaft door on the closed side. My customer has had a couple incidences with the elevator not operating because one of the shaft doors has failed to fully close and close the contacts. I'm looking for the circuit these 4 door switches are used in so I might be able to attach an LED to show the customer which door is the issue. Thanks
The locks are all in series you would have to modify the circuit to tell which door is open. Better off spending the time adjusting the doors properly so they close and latch properly.
1 member likes this: lowoil
Bobbybolognie
Bobbybolognie
Would you please send me a copy of the circuit. I'd like to install an LED at the end of the line. Thanks
PHP: 8.3.33 Page Time: 0.042s Queries: 33 (0.015s) Memory: 3.0369 MB (Peak: 3.5923 MB) Data Comp: Off Server Time: 2026-09-21 19:18:20 UTC
