Topics7,432
Posts41,135
Members10,097
Posts: 14 |
I've got a 50-04 that will randomly throw a 1516 ETSD system fault. Things I have tried: Hoist-way scan with IMS Redid the ETS tables with a TBS command. Replaced the ETS vain Reader. (when TKE did the MOD it still had the original blue Dover photo cell reader) Replaced the governor mounted encoder. (rust covered) Replaced the ENCINT2 PCB 6300ax1 Hoist-way scan clears every time TBS clears every time It seems to almost always happens coming into the first floor. Once it stopped leaving the first floor. Sometimes it will be accompanied by a 1007 fault but not always.
Any help greatly appreciated, I'm starting to pull my hair with this one Wes
Posts: 647 Likes: 7
Posts: 647 Likes: 7 |
If this unit uses the tape and magnets, check to see if the magnets are secured and properly placed. They’ve been known to drift downwards and a tad sideways. You should see a full length silicone bead on one side of the magnet at the minimum. A hoist way scan vs a high speed run into the terminal floor just might be a signal race giving the trouble.
Posts: 14 |
It does not use a tape and magnet. It uses the original Dover system that has a photo cell reader for DZ, UL, DL, and another photo cell reader for terminal limit veins.
Posts: 647 Likes: 7
So photo cell readers- my bad, I see you stated that in your original post. Is it possible to increase the normal slowdown count to see ETS point later? Compare top NTS/ETS values to bottom?
Posts: 1,769 Likes: 12
Posts: 1,769 Likes: 12 |
Try replacing the IOC card. I had an almost identical problem.
Posts: 14 |
I know i have tried changing the down slowdown count way longer and the car does not change how it runs. Should be slowing down 4 floors early but still runs in as if i changed nothing. I know in my version of IMS looking at the hoistway screen only shows we floor heights. Nothing ever changes in the slowdown information. I can dive it a ETSB, and ETST command and those values are almost the same top and bottom. I will check into the IOC board.
Posts: 14 |
I am still working on this issue. currently having trouble getting the main IOC card in controller. Will try to update when i have more information.
Posts: 14 |
UPDATE: So i have replaced the IOC and Cartop CWIK cards. Now i can't get the car to even pass a TBS setup. Shows NTSD failed. No Faults in the system other that a 847 E/NTSD setup failed. I can see the Egood, Ebad lights flickering as it hits the terminals. looking at the vain reader it appears to be centered on all vain's.
At what point did it go from an intermittent problem to a constant problem? If it was replacing one of the boards can you put the old one back and get back to the intermittent problem? Which IOC card did you have and which did you install? A 16 bit CPU can not go to a VH8 IOC card. Needs a VH3 or VH5.
Posts: 14 |
Hopefully this is the last update. The IOC card i was sent was a VH8 but the controllers have been updated at some point to 32bit. The last thing I changed was the encoder on the motor and the car has been running for a week. I'm not sure how the motor encoder and governor encoder work together for position in hoistway but it appears to have resolved the problem. Thank you all for the input.
That is baffling… as far as I know the motor encoder should have zero to do with that
Posts: 14 |
I agree, I couldn't find any information pointing to the motor encoder either. We happened to find a new one in a storage box and figured why not give it a shot. Car is still running.
I’ve been waiting to hear back. I thought for sure it was a 16 bit controller with a VH8 IOC card.
Posts: 14 |
I’ve been waiting to hear back. I thought for sure it was a 16 bit controller with a VH8 IOC card. It was A VH8 card they sent but there is stickers all over the controllers indication that it has been updated to a 32 bit controller.
That’s fine then, it was probably a VH8 anyway. Are these some official looking stickers or label maker labels? Just curious because I’ve never seen a sticker like that
Posts: 38 |
We have 2 cars identical machines and GOV. Intermittently get a 1613/1509 fault.
The car that runs without issues has P16=252. This car has P16=245.. Changed to 252 did a hoistway scan but my NTSD fails. Went back to 245 and NTSD still fails! Any ideas?
Did you do a backup scan after changing P16? TBS
Posts: 38 |
Yes, it goes through process, but fails with 847 fault. The car runs terminal to terminal with out faults, fails to save TBS.
